IEC 60335-2-40:2018 Household and similar electrical appliances - Safety - Part 2-40: Particular requirements for electrical heat pumps, air-conditioners and dehumidifiers
IEC 60335-2-40:2018 deals with the safety of electric heat pumps, including sanitary hot water heat pumps, air conditioners, and dehumidifiers incorporating motor-compressors and hydronic fan coils units, their maximum rated voltages being not more than 250 V for single phase appliances and 600 V for all other appliances. Partial units are within the scope of this International Standard.
This edition includes the following significant technical changes with respect to the previous edition:
- Clause 1 – limiting A2L refrigerants to those of a molar mass of more than or equal to 42 kg/kmol;
- Clause 7 – added requirements for A2L refrigerants,
- Clause 7 – added requirement for pre-charge pipe sets, detection systems, ventilation and the resulting charge;
- Clause 7 – added requirements for UV-C systems;
- Clause 7 – added requirements for transcritical refrigerating systems;
- Subclause 19.7 – amended text to match the intention of the subclause;
- Clause 21 – added requirements for transcritical refrigerating systems;
- Subclause 22 – added requirements for A2L refrigerants;
- Subclause 22– added detection systems;
- Subclause 22 – added new requirements for enhanced tightness refrigerating systems;
- Subclause 22 – added new requirements for UV-C;
- Clause 23 – added new requirements for UV-C;Clause
- Clause 24 – added requirements for transcritical refrigerating systems;
- Subclause 24 – added requirements for detection systems and airflow;
- Clause 32 added new requirements for UV-C;
- Annex BB – revised to add surface temperatures;
- Annex DD – added requirements for A2L refrigerants and amended requirements for flammable refrigerants to exempt A2L refrigerants;
- Annex GG – added requirements for A2L refrigerants;
- Annex GG.1 – amended Table GG.1 and related wording
- Annex GG.7 – added requirement to test;
- Annex GG.8 to GG.13 – new coverage for A2L refrigerants;
- Annex HH – revised to take into account A2L refrigerants;
- Annex JJ – new coverage of allowable opening of relays and similar components to prevent ignition of A2L refrigerants;
- Annex KK – new coverage of test method for hot surface ignition temperature for A2L;
- Annex LL – new coverage of refrigerant detection systems for A2L Refrigerants;
- Annex MM – new coverage of refrigerant sensor location confirmation test;
- Annex NN – new coverage of flame arrest enclosure verification test for A2L refrigerants;
- Annex OO – new coverage of UV radiation conditioning
- Bibliography – added new references.
This part 2-40 is to be used in conjunction with the latest edition of IEC 60335-1 and its amendments. It was established on the basis of IEC 60335-1:2010, its Amendment 1:2013 and its Amendment 2:2016.
|
|